XBuilder/Graphics Editor and displaying negative values in a Xenta 511.
  • XBuilder/Graphics Editor and displaying negative values in a Xenta 511.
  • Anonymous user
‎2018-09-06 02:52 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-05-28 06:51 AM
Negative values are displaying *** asterisk instead of the value.
TAC Vista
  • XBuilder 1.6
  • Vista 4
  • OGC Graphics
To display negative values in XBuilder, add a placeholder for the negative value.
In the example of terminal load, the lowest expected negative value is -100. This will require an integer value of 4 in the graphics editor in order to display -100.
If you the integer value is set to 3 and the value goes to -100, the display will show *** . This indicates the value is out of range according to the parameters set.
  • 2879