Proxy objects were successfully created in a G3 obix integration of a R2 station.  The writable proxy objects (ie: setpoint overrides) in the G3 station do not propagate the new value to the native object in the R2 station.
Niagara G3
Niagara R2
This is a known issue with the G3 obix driver.
Right-click the proxy object in the G3 station and do a 'forceUpdate'.
If there are several dozen proxy objects affected, download this program object.  Paste it anywhere in the Obix Network and execute it.  A 'forceUpdate' will be done to all proxy objects.
As of June 2013, these are the most up to date jar files for an obix integration:  2.301.535i.beta.jar, 2.301.535i.beta.jar.pc, and niagaraDriver.zip.
Extraction password:  niagara (all lowercase)