Workstation does not display in the Continuum Explorer object tree, but can be seen in listview
  • Workstation does not display in the Continuum Explorer object tree, but can be seen in listview
  • YangboLIU
    YangboLIU
‎2018-09-06 01:24 PM
There are several workstations in a LAN network. Some workstations can display correctly in the Continuum explorer object tree, but some workstations can not. All of the workstations can display in the listview. All the devices can do teach correctly.
  • Windows XP Sp3
  • Continuum 1.92
The outofservice check box has been checked
  1. From the listview, select the workstation which can't display correctly
  2. Right click on the workstation and select open
  3. From the general page, uncheck outofservice
  4. Restart Continuum.