Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Workplace Tech error "Server Busy" when trying to configure communications.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Workplace Tech error "Server Busy" when trying to configure communications.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Kim_Baze
    Kim_Baze
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2500 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Workplace Tech error "Server Busy" when trying to configure communications.

Picard Product_Support
‎2018-09-10 05:02 AM

Issue

Workplace Tech error POP-UP "Server Busy.... action can't be completed because the other program is busy. Choose 'switch to' to activate the busy program and correct the problem."  when trying to configure communications.
 

Environment

Workplace Tech Tool, revision 5.x 

OpenLDV 3.40

OpenLDV 4.0

Cause

Possible causes:

1. Multiple versions of Echelon drivers installed.

2. WinPcap may have been uninstalled, quarantined, or blocked.

Resolution

Only one version of LDV32.DLL should exist on the system and it should be the latest version. 

WorkPlace Tech 5.7 and later uses OpenLDV 3.40 or OpenLDV 4.0.

Verify the following:

  1. OpenLDV 3.40 or later is the only Echelon driver installed in the Windows Control Panel Add/Remove Programs dialog.  If the LonWorks PCLTA-20/PCC-10/PCLTA-10 for Windows is installed, do the following:
    1. From the Control Panel, Add/Remove programs, uninstall the OpenLDV driver
    2. Uninstall the PCLTA-20/PCC-10/PCLTA-10 for Windows driver.
    3. Reinstall the OpenLDV driver.
  2. Search the hard drive to locate all LDV32.DLL files on the pc.   Make certain all the LDV32.DLL files found are the same version as is found in the \LonWorks\Bin folder.   
  3. Verify the LON Flow Balance still communicates, if applicable.
  4. Verify winpcap 4.1.2 installed.  Use the link below to download and install WinPcap, if required.

 http://www.winpcap.org/install/default.htm

 UNCHECK THE FOLLOWING DURING INSTALLATION, UNLESS YOU HAVE UAC (User Account Control, in Windows 7 and Windows Vista) ENABLED!  If UAC is enabled, the checkbox should be CHECKED!

Uncheck Automatic startup

Labels (1)
Labels:
  • TAC IA Series
Tags (4)
  • Find more articles tagged with:
  • 6598
  • clsid
  • instance
  • wpt
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore