Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

WorkPlace Commissioning Tool does not find any devices on a BACnet-IP or BACnet-Ethernet network.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • WorkPlace Commissioning Tool does not find any devices on a BACnet-IP or BACnet-Ethernet network.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2424 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

WorkPlace Commissioning Tool does not find any devices on a BACnet-IP or BACnet-Ethernet network.

Picard Product_Support
‎2018-09-06 01:28 PM

Issue

When attempting to run the WorkPlace Commissioning Tool using the BACnet-IP or BACnet-Ethernet protocols, the search stops immediately and the "sweeping flashlight" is not displayed.  No BACnet devices are found.

Environment

Windows 7 Professional operating system

WorkPlace Tech Tool software version 5.7.4 through 5.7.7 and 5.8

Cause

The WinPcap ethernet communications driver could not be started causing the network search to fail silently.

During the installation of the WinPcap software, the installer presents an option to start the WinPcap driver at boot time.  Due to potential security concerns, it is suggested that this driver be configured not to start automatically when the computer is booted.  When the WinPcap driver has been installed in this mode and the user does not have system administrative rights, the driver cannot be started automatically when needed.  This issue and the required actions were documented in the WorkPlace Tech Tool 5.7.4 and 5.7.5 release notes.

Resolution

As published in the release notes document, there are two different ways the issue can be handled.

  1. Turn off Windows U.A.C. (Not recommended for security conscious users)
    1. Open the Windows control panel and select User Accounts.  If the control panel display is organized in the "Category" view mode, select "Add or Remove user accounts" then select the "Go to the main User Accounts page" link.
    2. Select "Change User Account Control Settings".
    3. Drag the displayed slider to the bottom position, "Never notify" then click [OK] to save the setting and exit.
       
  2. Configure the three WorkPlace Tech Tool programs to run with administrative rights. (May not be allowed on some customer owned computers).  NOTE: When the WorkPlace Tech Tool programs have been configured in this manner, the User Account Control screen stating "Do you want to allow the following program to make changes to this computer" will be displayed each time one of these programs is run. It is necessary to click the [Yes] button to allow the program to run.
    1. From the Windows start menu or from the desktop select "Computer".
    2. Navigate to the folder "\Program Files\WorkPlace Tech" on the local disk C: (or the local disk where the WorkPlace Tech Tool software was installed.
    3. Right-click on the application WPCT (may be shown as WPCT.exe) and select Properties from the displayed list.  Click on the "Compatibility" tab then click the button [Change settings for all users].  In the "Privilege Level" section, check the box "Run this program as administrator".  Click [OK] to save the change and close the "All Users" compatibility options window.  Click the [OK] button to close the properties window.
    4. Right-click on the application WPFB (may be shown as WPFB.exe) and select Properties from the displayed list.  Click on the "Compatibility" tab then click the button [Change settings for all users].  In the "Privilege Level" section, check the box "Run this program as administrator".  Click [OK] to save the change and close the "All Users" compatibility options window.  Click the [OK] button to close the properties window.
    5. Right-click on the application WPTech (may be shown as WPTech.exe) and select Properties from the displayed list.  Click on the "Compatibility" tab then click the button [Change settings for all users].  In the "Privilege Level" section, check the box "Run this program as administrator".  Click [OK] to save the change and close the "All Users" compatibility options window.  Click the [OK] button to close the properties window.
    6. Close the Windows explorer window.

In the event that a customer's security policy prohibits either of these methods of security permission control, the alternative is to uninstall the WinPcap program and reinstall it (by running the WorkPlace Tech Tool installer), configuring WinPcap to start automatically when the computer is booted.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5838
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore