Issue
System error log are reporting Wm_TimeObject errors when trying to create or modify a time schedule in a Xenta server.
- Wm_TimeObject: Http_Get Error (Error#:41992)
- Wm_TimeObject: Http_Post Error (Error#:41993)
-
Wm_TimeObject: Update File Error (Error#:41994)
Environment
- Xenta Server
- Xenta 511, 527, 711, 731
- Time Schedules
Cause
Attempting to view or create a time schedule object page in the web browser when the time schedule resides in an offline Xenta controller.
Resolution
The Xenta controller must be online to create or modify a time schedule.