Will changing the IP address of a BACnet/IP controller affect communication between BACnet objects on an established network?
  • Will changing the IP address of a BACnet/IP controller affect communication between BACnet objects on an established network?
  • sesa116873_brid
    sesa116873_brid
‎2018-09-06 12:24 PM
Niagara R2 and G3, UNC-520, ENC-520, WorkPlace Tech Commissioning Tool, MNB-1000
BACnet communicates using the BACnet device’s instance number, so changing the IP address of the controllers will not affects the communications between BACnet points. The BACnet/IP controller's MAC Address is comprised of its IP address and port number. This BACnet/IP Controller’s MAC address will automatically updated whenever one of the following tree procedures are performed, a “whoIs” is in R2, a “Discover” in G3 or a "Browse" of the BACnet/IP network in WorkPlace Tech Commissioning Tool.
  • TAC IA Series
  • 7852