Issue
Why does only one Exception mode work in TAC Xenta 121-FC/HP, even if the conditions for more than one Exception mode is fulfilled?
Environment
TAC Xenta 121-FC, TAC Xenta 121-HP
Cause
In TAC Xenta 121-FC/HP, with system program version up to 1.25, only one Exception mode could be active at the time.
It will always be the exception mode with the lowest number that will be activated.
For devices with system program version 1.26 and above, more than one Exception mode could be active.
Resolution
If the conditions for more than one exception mode are fulfilled, only the exception mode with the lowest number will be activated, for system program version up to 1.25..