Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

While trying to connect to a BACnet/Ethernet network with Workplace Commissioning Tool, the following error appears: "An error occurred while open communications. Please verif...

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • While trying to connect to a BACnet/Ethernet network with Workplace Commissioning Tool, the following error appears: "An erro...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1490 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

While trying to connect to a BACnet/Ethernet network with Workplace Commissioning Tool, the following error appears: "An error occurred while open communications. Please verif...

Picard Product_Support
‎2018-09-06 02:55 PM

Issue

While trying to connect to a BACnet/Ethernet network with Workplace Commissioning Tool, the following error appears:  

"An error occurred while open communications. Please verify communications settings and try again."

Environment

  • Workplace Commissioning Tool
  • BACnet/Ethernet network

Cause

Workplace Tech and WorkPlace Commissioning Tool use the NDIS BACnet Ethernet Packet driver to connect to BACnet/Ethernet networks. This driver's file name is KPF.sys and is known as a Kernel driver. If this file is not installed correctly or is halted by another program, BACnet/Ethernet will not function.

Resolution

To identify if Kernel driver is the issue, follow the steps below:
 

  1. Open system information from Windows - Accessories - System Tools - System Information
  2. Navigate to Software Environment - System Driver
  3. Look for KPF in the name column. If it is not there, re-install WorkPlace Tech as an administrator.   Make sure there is no software running that might not allow this file to be loaded.  Some virus software may also block the installation.
  4. If this file is there, check the state column to verify that it says running. Note:  this driver will only say running if BACnet/Ethernet is being used.
  5. If the file is there but it is not running, ensure that the actual location of the file in Windows Explorer is the same as the file column location in System Info. If they are not, then copy the file to the location listed in System Info.
  6. To verify that this driver is working correctly, use the net start command at a command prompt (type "net start kpf"). If the driver is working, it will indicate that it is already running.

As this is a Kernel level driver, if the above steps do not resolve the  issue, un-install WorkPlace Tech and re-install ensuring a local administrator account is used.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2739
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore