Where can I find information on lighting controller programming?
  • Where can I find information on lighting controller programming?
  • sesa139513
    sesa139513
‎2018-09-06 11:48 PM
I/NET Site
It is outlined in the System Operator Guide, TCON 207 for I2K rev 1.XX, TCON 236 for rev 2.XX, chapter 15 for both. There is some additional information, such as the addresses for zone points, are limited to 1200-1507. Another specific is, the control descriptors for the zone, must have the first of the pair equal a value of one. The control descriptor for the circuit points, need the first of the pair to equal a value of zero. There is an example save file in all host soft wares, sav subdirectory, named DEF7780.sav. A person should copy this file, rename it to their controller address and load it, to view examples of points.
  • TAC INET
  • 1282