When upgrading the MNB-1000 firmware from v1.32 to v1.4, the value of property APDU Retries changes to 0. This will cause problems with any MNB-1000 that make BACnet requests.
  • When upgrading the MNB-1000 firmware from v1.32 to v1.4, the value of property APDU Retries changes to 0. This will cause pro...
  • sesa119747
    sesa119747
‎2018-09-06 02:54 PM
  • MNB-1000 v1.32
Firmware v1.4 change APDU Retries to 0, which the value needs to be to 2 or 3.
Set the value of APDU Retries to 2 or 3 using WorkPlace Commissioning Tool or any other tool capable of changing that property.
To change the APDU retries follow these steps:
  1. Open WorkPlace Commissioning Tool
  2. Discover MNB-1000 and select its properties
  3. Select the Advance Tab
  4. Change the APDU retries to 3
  5. Select OK then restart the MNB-1000
Note: If there problems with COV, make sure this property is set to a value of 2 or 3.
  • TAC IA Series