When the WorkPlace Commissioning Tool browses a network or internetwork, not all controllers on the network will be found.
  • When the WorkPlace Commissioning Tool browses a network or internetwork, not all controllers on the network will be found.
  • sesa119747
    sesa119747
‎2018-09-06 02:55 PM
Increase the reply timeout value in WorkPlace Commissioning Tool
If controllers are missing from the list, the recommendation is to
  1. Refresh the list after the first attempt
  2. Increase the reply timeout value in the WorkPlace Commissioning Tool to 40,000 milliseconds or greater.
With large quantities of controllers (for example 80 or more), wait for the entire reply timeout value to expire for the list to stabilize.
  • TAC IA Series
  • 2713