When running SevenReports a C++ Run time error whether the report is Archive data or database data requested yyyy-mm-dd hh:mm:ss

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • When running SevenReports a C++ Run time error whether the report is Archive data or database data requested yyyy-mm-dd hh:mm...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3240 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

When running SevenReports a C++ Run time error whether the report is Archive data or database data requested yyyy-mm-dd hh:mm:ss

Picard Product_Support
‎2018-09-06 01:48 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:27 AM

Issue

Running SevenReports a C++ Run Time error. Happens either in Archive data reports or database reports

yyyy-mm-dd hh:mm:ss

Environment

I/NET Seven version 2.16 to current

Cause

Scope of Data yyyy-mm-dd hh:mm:ss

Resolution

 

 The C++ Runtime error or crash of SevenReports is due to a timeout problem because the archived data is so much information. What you will need to do is a couple of things listed below:

Run the archive file SevenReport or ArchiveSevenReport file with the following steps in mind
1. If using Archived reports, mount the archive file with the desired dates to search
2. when the date range comes up on the screen, offering to search with date, hour, minutes, and seconds yyyy-mm-dd hh:mm:ss limit the time range. The whole key here is to limit the time range. Example of range is below.
 
In other words, search for only 2 minutes on just one day. Do not put in three days, or three hours. Only search within a very limited search window. The crash occurs because there are huge archive or database entries with thousands of transactions that have to be sorted and searched through.

The crash was due to the report program attempting to generate a report with to much data to sort through. Be patient. Even on old computers, with XP, 500MB or RAM, and limited resources, the reports will be produced. 

Time and time again, this issue comes across. Using my old computer in the lab, the database from the customer is loaded, the archive files are loaded and still it works every time. The C++ Run Time error appears when expanding the search to more data and crashed the report. But limiting the amount of time to minutes or perhaps one hour, produces a report. (For an example of unusual examples: there have been 2 minutes of time for the search criteria, and 38,000 pages of report produced.)  
 
2010-08-16 09:00:00 until 2010-08-16 09:02:00
 

One thing you may want to look into at your site if you are experiencing large amounts of data for reports is Scan Interval. Read TCON300 for more info.
Information on Scan Interval and how this information is collected in the database. This is important because the more data you collect, the faster the scan rate interval, the more data will be in the reports.
Input and Output Points Point Database Parameters
 
The Scan Interval field is used with all point types. Enter a number between 1 and 255. This is the length of time in seconds that elapses between point scans.
 
If the point is an external input point, the controller scans the point at the interval you specify here, and updates its state/value in RAM memory of the DCU.
 
If the point is an external output point, or an internal input or output point, the scan interval determines how often a calculated point equation controlling the point (if applicable) is processed.
 
If the point is an indirect input or output point, the scan interval governs the time it will take to go to the “old data” state.
 
The default scan interval is 10 seconds for input points and 60 seconds for output points. All points can have their own unique scan intervals. All external discrete input points are scanned for discrete contact changes at 100 millisecond intervals.
 
Note: Defining an individual scan interval reduces available RAM memory in the DCU by approximately four bytes. You can conserve DCU memory by using the same scan interval for multiple points.
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5463
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore