When interfacing Veris pressure transmitters (PXP-xx-02S-T1) with a 0 to 5 vdc output signal to a universal input of a MNL controller instead of seeing 0 vdc with 0 pressure the UI...
  • When interfacing Veris pressure transmitters (PXP-xx-02S-T1) with a 0 to 5 vdc output signal to a universal input of a MNL co...
  • sesa119747
    sesa119747
  • Kim_Baze
    Kim_Baze
‎2018-09-06 02:41 PM
When interfacing Veris pressure transmitters (PXP-xx-02S-T1) with a 0 to 5 vdc output signal to a universal input of a MNL controller instead of seeing 0 vdc with 0 pressure the UI is seeing .5 vdc.
  • Veris pressure transmitters (PXP-xx-02S-T1)
  • MNL Controller
This is a compatibility issue with the Veris transmitters.
Veris Technical Support suggests putting a 2.2k ohm resister across the OUT and COM of the transmitter. This has been confirmed to resolve the issue by field personnel.
  • TAC IA Series