When emailing an alarm from the ENC the timestamp is always the time the alarm occurred; even when the Alarm email is due to an acknowledgement or return to normal.
  • When emailing an alarm from the ENC the timestamp is always the time the alarm occurred; even when the Alarm email is due to ...
  • Kim_Baze
    Kim_Baze
‎2018-09-06 09:58 AM
G3, ENC's, JACE's
The default "body" property of the EmailRecipient contains only the %timestamp% which represents when the alarm occurred.
Additional parameters can be added to the EmailRecipient "body" property to provide the "return to normal" and "acknowledged" timestamps. The return alarm timestamp can be added with %normalTime%. The acknowledged timestamp can be added with %ackTime%.
  • TAC IA Series