When compiling a WorkPlace Tech application, the error message "Error-Failed to create nci file" appears.
  • When compiling a WorkPlace Tech application, the error message "Error-Failed to create nci file" appears.
  • sesa119747
    sesa119747
  • sesa116877
    sesa116877
‎2018-09-06 02:57 PM
WorkPlace Tech
NCIs value is out of bounds.
Typically, this occurs when an out-of-range "NA" or "NaN" value is written to a NCI by a Niagara station, LonMaker, LNC or some other head-end device. If this issue occurs, check the values of all NCIs on the application drawing.  Any NCI displaying out-of-range values (i.e. 1.#QNaN, 1.#INF or etc.) should be reset to normal values or "NA".
  • TAC IA Series
  • 2649
100% helpful (2/2)