Issue
When attempting to build connection to a Filemaster the error "invalid I/NET seven operator" is given
Environment
I/NET
Filemaster Equalized client
Cause
When building a connection to a remote database, you must use the credentials for the remote PC not the local PC. In this example, when creating the connection to a Filemaster from a Equalized client, you must use the I/NET log in credentials for the Filemaster.
Resolution
Change the I/NET user name and password to one that has full permissions on the Filemaster PC. You may need to attempt to log into the filemaster PC to verify the username and password.