When Swiping on Reader of Door 3 or Door 4 on one SCU1284, Door 1 or Door 2 will be Open Instead
  • When Swiping on Reader of Door 3 or Door 4 on one SCU1284, Door 1 or Door 2 will be Open Instead
  • sesa145087_brid
    sesa145087_brid
‎2018-09-06 11:17 AM
When swiping on reader of door 3 or door 4 on one SCU1284, door 1 or door 2 will be open instead. The transaction shows "Reader Exit".
I/NET
Door 1 or door 2 is set to dual direction entry. So the reader on door 3 or door 4 is regarded as the exit reader of door 1 or door 2.
Set the "Exit Reader" option for the door to "None".
  • TAC INET
  • 11028