What should I set the Access Server System variable to on Continuum access controllers?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What should I set the Access Server System variable to on Continuum access controllers?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • ScottLeedberg
    ScottLeedberg
  • Carl_Slack
    Carl_Slack
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2017 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What should I set the Access Server System variable to on Continuum access controllers?

Picard Product_Support
‎2018-09-06 03:03 PM

Issue

What should I set the Access Server System variable to on Continuum access controllers?

Environment

CX9200, CX99xx, ACX57xx or CX9702 controller with an ACX780 or ACX700 controller.

Access Server, AccessServer

Cause

Below are the different configurations and what their different AccessServer system variable settings mean. Unlike Infinity when changing the setting in the controllers the controller does not reset. It is best if you set the AccessServer setting to the ACC Net ID of the Primary Access server workstation. This will keep the Access Control system operational should there be any distribution problems.

Resolution

CX9200, CX99xx,  or CX9702 controller with an ACX780 or ACX700 controller.

The CX can stay at the default of it’s own ACC Net ID. In the above configuration the AccessServer variable in the CX is ignored. The AccessServer variable in the ACX controller can be one of the following:

  1. AccessServer value set to 0 in the ACX (Default setting).This means that access validation of personnel records will only be done locally in the ACX. If the person is not found in the ACX or the person is denied access locally in the ACX the person will not get in.
  2. AccessServer in the ACX controller set to the ACC Net ID of the Primary Access Server workstation (valid values are 191-253). This means that access validation of personnel records will be done locally in the ACX first. If the person is not found in the ACX or if the person is denied access the controller will double check at the workstation to verify whether or not the person is supposed to have access. If the person is also denied access at the workstation then the person will not get in.
  3. If the AccessServer value in the ACX controller is set to the ACC Net ID of the parent CX controller it has no effect and is ignored.

CX99xxor CX9680 controller with AC1 modules  or ACX57xx.

The CX can stay at the default of it’s own ACC Net ID. 

  1. AccessServer value set to the CX’s own ACC Net ID (Default). This means that access validation of personnel records will only be done locally in the CX. If the person is not found in the CX or the person is denied access locally in the CX the person will not get in.
  2. AccessServer value set to the ACC Net ID of the Primary Access Server workstation (valid values are 191-253). This means that access validation of personnel records will be done locally in the CX first. If the person is not found in the CX or if the person is denied access the controller will double check at the workstation to verify whether or not the person is supposed to have access. If the person is also denied access at the workstation then the person will not get in.
  3. AccessServer value set to 0. This is not a valid setting for a CX controller.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2108
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore