A 0-10 Vdc sensor will be wired into a MNL/MNB controller.  The voltage must be dropped from 0-10 Vdc to 0-5 Vdc to interface and read properly.  What's the part number for ordering the voltage divider used to achieve this task?
MNL controllers
MNB controllers
Another manufacturer's sensor designed with a 0-10 Vdc control signal.
The part number is AD-8961-220.  It is available for purchase via iPortal (http://iportal2.schneider-electric.com).
The controller analog input object would be set up as follows:
Linput= 0.909 Vdc
LScale= 0
Hinput= 4.545 Vdc
HScale= 100