Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What requirements must be met to allow the WorkPlace Tech Tool software to monitor a previously installed application?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What requirements must be met to allow the WorkPlace Tech Tool software to monitor a previously installed application?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Kim_Baze
    Kim_Baze
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1928 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What requirements must be met to allow the WorkPlace Tech Tool software to monitor a previously installed application?

Picard Product_Support
‎2018-09-06 10:04 AM

Issue

If the WorkPlace Tech Tool application file has been modified when you attempt to monitor a controller containing that application, blank or incorrect monitor tag values will be displayed.

Environment

WorkPlace Tech Tool software versions 5.0 through 5.8.2 or 5.8.6

MNL or MNB controller loaded with an application downloaded from WPT

Visio 2003, Visio 2007 or Visio 2010

Cause

There are two causes:

First, the WPT software, release 5.8.3, 5.8.4 or 5.8.5 will modify the application when it is opened making it appear to be different than the previously downloaded application

Second, failure to observe the following three constraints, regarding the application .vsd file will make the application file appear different than the application previously downloaded:

  • The application file (.vsd) must not have been modified and/or re-saved in any version of the WorkPlace Tech Software since the application was downloaded.
  • The application file (.vsd) must not have been modified directly in Visio and re-saved.
  • The application file (.vsd) must have been last saved, compiled and downloaded using any version of the WorkPlace Tech Tool software, 5.0 through 5.8.2 or 5.8.6, running in Visio 2003, 2007 or 2010.
     

Resolution

An application downloaded to an MNL (or with the compatible WPT version, MNB) controller can be monitored provided that the application .vsd file has not been modified or re-saved after download and that the current version of the WorkPlace Tech Tool software, versions 5.0 through 5.8.2 or 5.8.6 (not versions 5.8.3, 5.8.4 or 5.8.5)  is being is being used with a compatible version of Visio (2003, 2007 or 2010).

NOTE: For MNB controllers this applies only to WPT versions 5.7.0 through 5.8.2 and 5.8.6 as the earlier versions are not compatible with MNB application development.

Labels (1)
Labels:
  • TAC IA Series
Tags (3)
  • Find more articles tagged with:
  • 14399
  • mismatch
  • tags
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore