What options are available to share public values across two LNS networks.
  • What options are available to share public values across two LNS networks.
‎2018-09-07 06:46 AM
Last Updated: Crewman ContentModerator ‎2025-09-25 03:26 AM
Have two LNS databases and need to share values between them.
  • Lonmaker
  • Newron NL220
  • Vista
As the two LNS networks are not connected you cannot bind values between them.
You can use a Object transfer in Vista or a Loytec L-Proxy controller
The main difference between the two methods is the object transfer is PC based and the Loytec option is field based.
Object Transfer option:
Add an object transfer as described in the Chapter 14 of the TAC Vista Technical Manual.
L-Proxy Loytec controller option:
This product will reside on both LNS channels and can be setup to transfer values across networks. Here is a link to the product .
From here scroll down to find the L-Proxy Datasheet
  • 4676