What is the pin out for a cable to commission a netcontroller (CX99xx)?
  • What is the pin out for a cable to commission a netcontroller (CX99xx)?
  • ScottLeedberg
    ScottLeedberg
‎2018-09-06 03:02 PM
CX99xx
Need to create a cable to commission a controller.
RJ Connector <- - - - -> 9 Pin RS232 PC Controller Comm3
Pin 1 - DTR <- - - - -> Pin 1 - CXD
Pin 2 - CTS <- - - - -> Pin 7 - RTS
Pin 3 - CXD <- - - - -> Pin 4 - DTR
Pin 4 - RTS <- - - - -> Pin 8 - CTS
Pin 5 - GND <- - - - -> Pin 5 - GND
Pin 6 - RD <- - - - -> Pin 3 - TD
Pin 7 - DSR <- - - - -> Pin 6 - DSR
Pin 8 - TD <- - - - -> Pin 2 - RD
On the RJ connector for the controller's comm3, Pin 1 is the furthest to the left with the insert clip facing away from you and the gold teeth facing you.