Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

What is the difference between "Enhanced MSTP" and "Standard MSTP" Token Passing in Continuum BACnet?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the difference between "Enhanced MSTP" and "Standard MSTP" Token Passing in Continuum BACnet?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • sesa101527
    sesa101527

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3420 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the difference between "Enhanced MSTP" and "Standard MSTP" Token Passing in Continuum BACnet?

Picard Product_Support
‎2018-09-06 02:54 PM

Issue

What is the difference between "Enhanced MSTP" and "Standard MSTP" Token Passing in Continuum BACnet?

Environment

Continuum BACnet

Cause

It is important to note that Only Continuum BACnet controllers have this feature. Any third party BACnet MSTP controller connected to a Continuum BACnet system will only perform Standard MSTP token Passing. In a network where you have Continuum B3 controllers and third party MSTP controllers and you have enabled Enhanced MSTP, you will have a combination of the two methods. The Continuum B3's will always pass the token back to the BCX, and the 3rd party controllers will always pass the token to the next ID on the MSTP. If you wanted the benefit of Enhanced MSTP on this type of a system, you could intersperse the MSTP ID's of the B3's and the third party so that you would have a more even flow of the token back to the BCX.

Resolution

Continuum Bacnet Controllers default to "Enhanced MSTP". What this means is that the Ethernet level controller (BCX or B4920) that manages the MSTP network sends out a message to all Continuum B3 controllers which tells them that after they are done with the token on the network, that they should pass it back to the BCX or B4920 instead of sending it to the next B3 down the line. The purpose of this is so that any user interaction with the B3 network such as graphics, listviews, reports, etc.. will be much faster. This Token passing scheme is similar to how Infinet performs.

Standard BACnet MSTP token passing is done such that each controller on the MSTP network gets the token equally and this includes the BCX or B4920. So if you had 127 nodes on the network, the BCX controller would only get a chance to talk once after every MSTP controller had a chance to talk. The Continuum BACnet controllers can operate in either mode by setting this feature in the BCX or B4920 Web Configuration page.

Each token Passing scheme has some benefits. If there were a lot of user interface type access needed on a system, the Enhanced mode would be preferable for speedy response.
If there was very little or no user interaction but there was a lot of data sharing or alarm delivery from the MSTP controllers, the standard token passing would give all the devices on the MSTP network more opportunity to export their data.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2776
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore