Due to various reasons it is sometimes necessary to bring into the Continuum DB a controller and its object (points, programs and possibly children controllers such as b3 or Infinet controllers) that have been configured in a different Continuum DB.
  1. Create the Controller object in the Continuum database and ensure controller comes online.
  2. Set the 'Send To Database Options' appropriately, for example make sure to select 'Save attached objects and controllers' to bring in field devices.
  3. Perform a save to database by right clicking on the controller and selecting 'Save to' \ 'Database'
  4. If BACnet controller (bCX4040), perform a 'Find new BACnet device from the root then do a send to database on the bCX and b3s to get the BACnet objects into the DB