What is the IP Network bandwidth requirement for a Continuum controller?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the IP Network bandwidth requirement for a Continuum controller?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2196 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the IP Network bandwidth requirement for a Continuum controller?

Picard Product_Support
‎2018-09-10 03:09 AM

Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM

Issue

What is the bCX and NCII required bandwidth?

10Mb, 100Mb Network Connections, GSM Modems.

Environment

Continuum Ethernet level controllers: ACX57xx, Netcontroller II and bCX1

Cause

IT Departments often ask for the required IP Network bandwidth for the CX and bCX controllers; as it is not listed on the datasheets.

Is there a bandwidth calculator available?

Resolution

The Network usage of a bCX/ CX/ ACX controller will vary constantly depending on what is happening on the system at the time. It will be affected by user commends, Graphics, Plain English programming, Access events, reloading or re-flashing controllers and time triggered events.

The 2nd generation controllers network connection supports a 10Mb half duplex or 100Mb full duplex auto sensing permanent connection.

Note: Older 1st generation controllers (CX9200, CX9400, CX9900 series) only support 10Mb half duplex.

So a corresponding up to 10Mb or 100Mb connection would be ideal.

GSM Modem or other packet based communication networks are unlikely to be able to provide the continuous data throughput required by Continuum.

In terms of bandwidth an absolute minimum of 1Mb in both directions is recommended but this will depend on the specific site requirements you have, for example if there is a requirement to update graphic or alarm values within a specific time then a 10Mb connection would be more appropriate.

The following Bandwidth Calculator can be used to determine the % network usage on a 10Mb network connection. This was created specifically for typical Access Control projects, so for HVAC applications the following should also be considered: data logging, PE programs passing data, IP based X Drivers.

Fill in the appropriate values in Column D for the system:

Bandwidth Calculator.

Labels (1)
Labels:
  • Andover Continuum
Attachments
Tags (2)
  • Find more articles tagged with:
  • 6193
  • speed
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore