What is the Actual SCU Power Requirement and Battery Life

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What is the Actual SCU Power Requirement and Battery Life
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1834 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What is the Actual SCU Power Requirement and Battery Life

Picard Product_Support
‎2018-09-07 01:15 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:25 AM

Issue

What is the Actual SCU Power Requirement and Battery Life expectancy

Environment

I/NET site with Access Control

Cause

SCU Power Requirement information

SCU Battery Life information

Resolution

The current power ratings listed in TCON312 & TCON313 are the indicate maximum power consumption for Agency markings and recommended transformer sizing.

All of the SCU models all have the same supply circuits.
All three models can deliver up to approx 1.2 amps of 13.6V, and .2A of 5V, along with the onboard 3.3V logic load.

The SCU1200 and SCU1280 provide two terminal blocks (TB4 & TB5) which can deliver 13.6V and 5V power out to miscellaneous sensor/detector loads.

The SCU1200 and SCU1280 also support an external a lead acid battery backup.

When this battery is discharged, application of AC power can call for maximum power from the 13.6V supply with the onboard supply limiting 13.6V to the battery and external load to currents up to approx 1.2 amps.

Even if you are not using the external power for sensor/detector power, the battery can pull maximum power during recharge.

If you are NOT using an external battery backup, and you are NOT using the external 13.6v connection (on TB4 & TB5), and you are NOT using the external 5V connection (on TB4 & TB5), then you could assume a reduced 24VAC power consumption as follows.

For the SCU1200, the 24VAC power input would be approximately .1A (2.4VA).

For the SCU1280, the 24VAC power input would vary from about .1A with no relays on, up to approx .3A (7.2VA) with all 8 relay outputs energized.


SCU Battery information:
SCU1284 NiMh Battery Life
The Varta battery datasheet lists the life expectancy for trickle charge applications (which is what the SCU uses) as
6 years (at temp of 20C)
and
3 years (at temp of 45C)
So in typical access control environment we should be around 25C so around the 6 year expectation would be appropriate.
Also, the end of life is frequently interpreted as reaching ½ capacity on a NiMh battery, so it still has memory retention, even at end of life. 

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 2993
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore