What if any voltage can be measured on a Micronet 2000 U-Bus?
  • What if any voltage can be measured on a Micronet 2000 U-Bus?
  • sesa119747
    sesa119747
  • WaynePeters
    WaynePeters
‎2018-09-06 02:40 PM
  • MicroNet 2000
  • U-Bus communication
Information about voltage helps implement multiple MicroNet 2000 controllers in U-Bus communications interface.
The U-Bus is a Wired-OR open collector communication bus talking at 2400 baud. The MN-ASDI has the U-Bus current source.  It supplies the current for the U-Bus communications. It should supply about 45 ma. with short circuit protection. Under normal communications, the U-Bus voltage will be around 15 volts +/- 2 volts when measured with a voltmeter.
  • TAC IA Series
  • 3320