What hardware can be used to replace the 7900 DPU Series?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What hardware can be used to replace the 7900 DPU Series?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1327 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What hardware can be used to replace the 7900 DPU Series?

Picard Product_Support
‎2018-09-07 01:05 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:25 AM

Issue

What is the replacement hardware for the 7900 Series security devices, DPU 7910, DPU 7920, DIO 7940 and DIU 7930.

Environment

Series 7900 DPUs. DPU 7910, DPU7920, DIU 7930 and DIO 7940.  

I/NET Seven.

Cause

Series 7900 door controller units are no longer available.  Replacement Hardware is the SCU 1200 Series.

Resolution

 Below is a table showing the comparison and replacement hardware for the 7900 Series controllers.  

Series 7900

Replacement

I/NET Seven Host Software Network Designation

MCU Type

Device Type

DPU 7910

SCU 1284

DPU

SCU 1284

DPU 7920

SCU 1284

DPU

SCU 1284

DIO 7940

SCU 1280

DIO

SCU 1280

DIU 7930

SCU 1200

DIU

SCU 1200

 
Notes: 
  1. To use the full input capacity of the SCU series, (12 DI), you must use the device in a double-address mode. When typically using them as a replacement for 7900 series the existing addressing usually restricts the use to single address mode. Refer to TCON312 for further information.
  2. Also be aware of I/NET system Compatibility, download TCON312 (Overview section) for further detail. 

Regardless of which version of TAC I/NET software you use, you must load SLIs with updated software in order to properly communicate with the SCU.  

Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 4847
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore