What does this BACnet error in the standard output window mean? Received bit string (25) is longer than expected length (23)
  • What does this BACnet error in the standard output window mean? Received bit string (25) is longer than expected length (23)
  • Kim_Baze
    Kim_Baze
‎2018-09-06 12:46 PM
Getting warning " Received bit string (25) is longer than expected length (23)" in the standard output window.  Is this a problem?
I/A Series R2 G3 BACnet Niagara
This warning is because the UNC was reading the list of object types supported from the device, and the device was implemented to a different protocol revision, in which there were a different number of object types defined.
The UNC ignores this, and it has no negative impact.
  • TAC IA Series
  • 7162