What are the valid ACCNet ID ranges for Controllers and Cyberstations?
  • What are the valid ACCNet ID ranges for Controllers and Cyberstations?
  • sesa139513
    sesa139513
  • PaulFr
    PaulFr
‎2018-09-06 09:48 AM
How many controllers and Workstations can Continuum systems support?
All Ethernet level controllers and Workstations.
bCX, CX, NCII, ACX
Valid address ranges required
Each "Network" (often called Continuum Network or Infinity Network) supports controllers with ACCNetID values of 1 to 190.
No duplicate numbers are allowed on the same network
Potentially the database supports up to 4 Million networks.
Cyberstation workstations have ACCNetID's in the range 191 through 254 (maximum 64)