What are the memory, CPU and I/O specifications for the MNB controllers?
  • What are the memory, CPU and I/O specifications for the MNB controllers?
  • Kim_Baze
    Kim_Baze
  • Julio_Cortes
    Julio_Cortes
‎2018-09-06 01:37 PM
I need to know hardware specifications for the BACnet controllers and cannot find it in any documents.
The specifications given below are accurate as of 6/30/2011 but are subject to change without notice.
The memory specifications below are also available in the MicroNet BACnet Wiring, Networking, and Best Practices Guide.  If a formal document for the CPU and I/O specifications is required contact your Regional Salesman or Product Marketing.
MNB-V1 and MNB-V2
Processor: Atmel ATMEGA256-16AJ (8-bit) operating at 16 MHZ
Memory: Flash 256KB, SRAM 8KB, EEPROM 4KB
A/D and D/A resolution: UI inputs have a 12 bit resolution and UO outputs have an 8 bit resolution
MNB-70
MNB-300
Memory: Flash 256KB, SRAM 8KB, EEPROM 4KB, FRAM 8KB
MNB-1000
Main Control
Processor: Freescale Coldfire MCF5485 (32-bit) operating at 200 MHZ
Memory: Flash 16MB, SDRAM 64MB, EEPROM 1KB, Boot Flash 2MB
Motherboard (Local I/O Processor)
Processor: Atmel ATMEGA128 series 8-bit microcontroller running at 16 MHZ
Memory: Processor Flash 128KB, SRAM 4KB, EEPROM 4KB.  Motherboard SRAM 256KB, EEPROM 128KB