Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

What are the System Requirements for installing MSDE or MSSQL server with a Niagara R2 Enterprise Server?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What are the System Requirements for installing MSDE or MSSQL server with a Niagara R2 Enterprise Server?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • sesa119747
    sesa119747
  • DavidFisher
    DavidFisher

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1592 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What are the System Requirements for installing MSDE or MSSQL server with a Niagara R2 Enterprise Server?

Picard Product_Support
‎2018-09-07 02:12 AM

Issue

What are the System Requirements for installing MSDE or MSSQL server with a Niagara R2 Enterprise Server?

Environment

  • Niagara R2 Enterprise Server
  • MSDE or MSSQL server

Cause

Hardware and Operating System (OS) must meet the minimum requirements to run MSDE or MSSQL server.

Resolution

These are the following minimum hardware and operating system requirements (per Microsoft’s web site) to run the MSDE database:

• Pentium III, 500-MHz or higher processor.
• Minimum of 512 MB of RAM, 1 GB recommended.
• Minimum of 1 GB of available hard disk space, 3 GB for applications that need more archiving capacity.

The following operating system configurations can run the MSDE:
• Windows XP Professional
• Windows NT Workstation 4.0 with Service Pack 5 or later Supported Software
Supported Database Implementations
• Windows NT Server 4.0 with Service Pack 5 or later
• Windows NT version 4.0 Server Enterprise Edition with Service Pack 5 or later
• Windows 2000 Professional
• Windows 2000 Server
• Windows 2000 Advanced Server
Microsoft asserts that the SQL Server 2000 Driver for JDBC (required for MSDE) has been tested and certified on the following operating systems:
• Microsoft Windows XP
• Microsoft Windows 2000 with Service Pack 2 or higher

The following versions of the JDK are supported for use with the SQL Server 2000 Driver for JDBC:
• JDK 1.1.8
• JDK 1.2
• JDK 1.3
The Microsoft SQL Server 2000 Driver for JDBC is available for download from microsoft.com to all licensed SQL Server 2000 customers at no charge. Review the end-user license agreement (included with the download) for further details on users’ rights.

Note:  A MSDE database can run on a machine other than the Enterprise Server and have the server station write data to the database. For information on the system requirements for a remote MSDE installation, visit http://msdn.microsoft.com/library. This configuration is not supported by Schneider-Electric. 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 2702
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore