What are the Linking Rules within the Niagara R2 platform?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What are the Linking Rules within the Niagara R2 platform?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa119747
    sesa119747
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1081 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What are the Linking Rules within the Niagara R2 platform?

Picard Product_Support
‎2018-09-06 02:40 PM

Issue

What are the Linking Rules within the Niagara R2 platform?

Environment

Niagara R2 platform

Cause

Additional information on linking rules to correctly linked objects.

Resolution

In most cases, in order for two properties to be linked, they must use the same data species. In a link, one object's output supplies the value (or trigger) used by the other object with the receiving input. The Link Editor in the JDE enforces this rule when selecting a property on one side of the window to link.  An exception to the need for matching data species occurs when linking Gx objects, which have only inputs.

For example, the "binding" input of a GxText object can be linked to any internal (configuration property) of another object, in addition to most output properties.  When linked to an internal property, a GxText object displays text showing the value of that property.  Unlike "normal" links, Gx object links are considered user-interface ("ui") links, not part of "control logic." Instead, they provide the building blocks of a user interface.

The Link Editor also enforces additional link rules. Many inputs can be linked to a single output as needed ("one-to-many").  For any input property that is already linked, no further link to it is permitted unless the property is a priorityArray type or trigger type (or certain types of Lon properties). Only then is a "many-to-one" link allowed.

External links (between stations) have further restrictions. The following types of external links are not permitted (nor are they shown in the Link Editor):

  • Links between prioritizedOutputs and priorityArray input properties.
  • Links between properties using triggerType data species.
  • Links from a GxText object to an internal property of another object (only inputs or outputs are available).
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3318
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of