Week Chart Value Hexadecimal Code

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Week Chart Value Hexadecimal Code
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1923 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Week Chart Value Hexadecimal Code

Picard Product_Support
‎2018-09-11 01:02 AM

Issue

How to decode the Week Chart Hexadecimal Value in Vista.

 

Point Name

TSCHED.TS09

Channel Name

DMAVISTA-LNS-DMA-Channel4-LTG_04_09

Object Name

Time Chart - TAC Xenta

Week Chart Value

00006270^00001C20^7F~00001D4C^00006270^7F

Interpretation

[7:00:00 AM - 2:00:00 AM, SMTWTFS] [2:05:00 AM - 7:00:00 AM, SMTWTFS]

   

Environment

Time Schedules

Cause

 A Hexadecimal Code is generated upon creation or modification of a time schedule.

Resolution

The Hex code represents seconds after midnight and days of the week, and days of the week that the schedule is on. 

An Excel spreadsheet to perform the conversion for you can be downloaded here.

In this Example:

[7:00:00 AM - 2:00:00 AM, SMTWTFS] [2:05:00 AM - 7:00:00 AM, SMTWTFS],  Is coded to be:
00006270^00001C20^7F~00001D4C^00006270^7F

Break down each bracket into parts, here is the first bracketed time elapse:

00006270^00001C20^7F

00006270 =7:00:00 AM
00001C20 =2:00:00 AM
7F=SMTWTFS

To decode 00006270 which represents 7:00:00AM:

00006270 (Hex seconds) =25200 (Decimal seconds)
25200/60 (seconds in a minute)= 420 minutes
420 /60 (minutes in an hour) = 7 hours
12AM midnight plus 7 hours is 7:00:00AM

 To decode 00001C20 which represents 2:00:00AM:

00001C20=7200
7200seconds = 120 minutes
120 minutes = 2 hours
2:00AM

To decode 7F which represents SMTWTFS

7F (Hex days of the week) =127 (decimal) =1111111 (binary)  = SMTWTFS

Each bit of a 7 digit binary value is used to represent the day on in the schedule…

S=1000000
M=1
T=10
W=100
T=1000
F=10000
S=100000

 

Here is another example:

0000003C^00000078^04
[12:01:00 AM - 12:02:00 AM, ---W---]

 3Ch=60, 78h=120, 04h=0001000

Labels (1)
Labels:
  • TAC Vista
Attachments
TAC Xenta Weekly Time Schedule Breakdown.zip
Tags (11)
  • Find more articles tagged with:
  • 12805
  • 1b83c=7
  • 62703c=1b8
  • 7am
  • all
  • alternatively
  • converting
  • decimal.
  • dividing
  • math
  • twice
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore