Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

We are unable to connect to a Niagara G3 ENC-520 whose IP address was incorrectly set. How can the IP address be determined and changed if there's no access via its Ethernet po...

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • We are unable to connect to a Niagara G3 ENC-520 whose IP address was incorrectly set. How can the IP address be determined a...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1353 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

We are unable to connect to a Niagara G3 ENC-520 whose IP address was incorrectly set. How can the IP address be determined and changed if there's no access via its Ethernet po...

Picard Product_Support
‎2018-09-06 10:37 AM

Issue

We are unable to connect to a Niagara G3 ENC-520 whose IP address was incorrectly set. How can the IP address be determined and changed if there's no access via its Ethernet port?

Environment

Niagar Workbench, ENC-520, ENC-410

Cause

Incorrect entry of the IP Address or subnet mask can cause the ENC to appear unresponsive to WorkBench software.

Resolution

There are two methods available to determine the IP address and subnet mask entered for the ENC.

The first method requires having access to the computer used to change the IP address of the ENC. Your Workbench PC records the “before and after” TCP/IP settings made from Niagara platform connections in a a file called "ipchanges.bog". You can review changes from Workbench using the following procedure.

Do the following in Workbench:
1. In the Nav tree, expand “My Host” and then “My File System.”
2. Expand “Sys Home” and then “users.”
3. Expand your user folder, then expand “ipchanges.bog.”
Child folders are “date-named” using the following convention:
d for example, “d20041220171000” for 2004 Dec 20 5:10pm
4. Expand any folder of interest. Underneath each folder are two objects:
   • priorValue — TCP/IP settings that existed before this change.
   • newValue — TCP/IP settings that existed after this change.
5. Double-click a priorValue or newValue to see settings in the “Tcp Ip Host Editor” (see Figure).


The second method requires the use of a terminal program, an UNCC-405 to adapt RS232 to RJ45, and a CBL-RJ45 cable (a standard Ethernet cable no longer than seven feet will do). The HyperTerminal program is used to directly connect to a ENC-520 to verify and to make changes to its IP address in order to make it accessible. HyperTerminal makes it possible to view the ENC's configuration and execute limited commands.

Reference the section “Using serial system shell”, located in Chapter 1 of the Niagara AX Install & Startup Guide, on how to directly connect to ENC using HyperTerminal. After connecting to the ENC, use the procedure "Updating Network Settings", which is located in the same Chapter of the guide, to display and/or change the IP address or subnet mask.

Failure to enter the subnet mask properly can prevent the UNC from being seen by WorkPlace Pro.
 

 

 

 

 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 12619
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore