Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Warning - Platform running low on RAM disk space (Niagara G3 Release 3.2.5 and higher)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Warning - Platform running low on RAM disk space (Niagara G3 Release 3.2.5 and higher)
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • WaynePeters
    WaynePeters
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3596 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Warning - Platform running low on RAM disk space (Niagara G3 Release 3.2.5 and higher)

Picard Product_Support
‎2018-09-06 02:39 PM

Issue

Warning - Platform running low on RAM disk space (Niagara G3 Release 3.2.5 and higher)

Environment

I/A Series G3 (typically embedded ENC/JACE platforms)

Cause

Low disk warning for history RAM disk A station fault will be generated if the free disk space on the history / alarm RAM disk falls below the minimum percentage specified on the PlatformServices property sheet.

Resolution

During station startup,  /niagara/bin/ramdisk.sh is invoked to create the RAM disk partition.   The RAM disk is named /aram0 and symbolic links are created from /alarm -> /aram0/alarm /history -> /aram0/history.  After the RAM disk is created it is populated with the contents of the alarm.zip and history.zip files.  During a station save or shutdown, the alarm and history files on the RAM disk are zipped and stored under the station directory in alarm/alarm.zip and history/history.zip. 

If this fault occurs, users should take one or more of the following actions to prevent history/alarm data from being lost:

  1. Reduce number of histories that you are collecting
  2. Reduce number of records in each history
  3. Increase history RAM disk system (requires reboot).

Action 3, above, will reduce the available system memory and should only be taken if there is sufficient free system memory.  Rather than writing history and alarm records directly to persistent storage, a Niagara G3 station stores history and alarm records in a RAM disk. This approach reduces the number and frequency of writes to flash.  Be careful not to increase too much otherwise you risk consuming all the available JACE free RAM causing the niagarad to crash.  Review the free system memory and make sure to leave a buffer of at least 1 MB of free RAM.  The RAM disk size is stored in /niagara/lib/platform.bog and can be adjusted using Services -> Platform Services.

After reducing the number of histories, etc. the RAM disk will still indicate a low warning message until the unused histories are removed from the history storage.  Delete the unused histories using the Database Maintenance view on the history component view within the station.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 3368
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore