Issue
In the conversion log when upgrading database, the following warning is logged:
Invalid value for ProgramID in the object, "~/LonWorks Local FT-10 Interface/Your Network/Controller Name/IO/IO Module Name". The default value has been applied.
Product Line
EcoStruxure Building Operation
Environment
- AS
- Device administrator
Cause
TAC Xenta IO modules of the model 411/421 does not have an application ID populated in the properties. All other IO modules do. The upgrade sees this as missing information.
Resolution
You can ignore this if the module is a TAC Xenta IO 411/412.