Warning: Invalid value for ProgramID. The default value has been applied.
  • Warning: Invalid value for ProgramID. The default value has been applied.
  • Benji
    Benji
  • sesa150555
    sesa150555
‎2018-09-06 09:00 AM
In the conversion log when upgrading database, the following warning is logged:
Invalid value for ProgramID in the object, "~/LonWorks Local FT-10 Interface/Your Network/Controller Name/IO/IO Module Name". The default value has been applied.
  • AS
  • Device administrator
TAC Xenta IO modules of the model 411/421 does not have an application ID populated in the properties. All other IO modules do. The upgrade sees this as missing information.
You can ignore this if the module is a TAC Xenta IO 411/412.
  • 17994