Vista error log - Netfunc error
  • Vista error log - Netfunc error
  • sesa150561
    sesa150561
‎2018-09-06 09:56 AM
Vista Workstation error log has "Netfunc errors."
  • Vista
  • Vista multi server system
The Netfunc message in the log means that the master node is already working on the subscription that the node is sending. This can be caused by an overloaded network. The node has not received an acknowledgement from the master in a timely manner. It could also mean that the Master and its node are not synchronised correctly.
If the error continues to appear in the log:
  1. Make sure the network is not overloaded.
  2. Close down the server and the nodes and restart them so they will resynchronize.
  • 14773