Vista database has a Xenta group with only LonWorks devices in it.
  • Vista database has a Xenta group with only LonWorks devices in it.
  • SESA116857
    SESA116857
‎2018-09-06 03:05 PM
TAC Vista System Plugin
Either due to operator error or software problems a LonWorks device can be added to a Xenta group in your Vista database. If you try to correct this in the System Plug In by removing the Xenta group and adding a new LonWorks group with the same name, an update Vista database command does not correct the problem.
  1. Delete the Xenta group or the new LonWorks group that shares the name
  2. Update the Vista Database.
  3. Once you have verified that the group no longer exists in the Vista database, add it again in the System Plug-in
  4. Update the Vista Database one more time
  • 2031