Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Vista central time chart and TAC Xenta Server time chart

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Vista central time chart and TAC Xenta Server time chart
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa150555
    sesa150555
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1640 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Vista central time chart and TAC Xenta Server time chart

Picard Product_Support
‎2018-09-06 12:28 PM

Issue

  • Vista central time chart and TAC Xenta Server  time chart - what happens when communication between Vista server and TAC Xenta Server is lost
  • When is TAC Xenta Server time chart updated from Central time chart?
  • Central time chart overwritten from TAC XBuilder

Environment

  • TAC Xenta 731, TAC Xenta 721, TAC Xenta 711, TAC Xenta 701, TAC Xenta 511. TAC Xenta 527, TAC Xenta 555
  • TAC XBuilder
  •  TAC Vista

Cause

The Xenta Server only knows about its own time objects that is defined in XBuilder (or TSCHI in Menta). There are no synch between the central chart and the local time object.

If you download the project from XBuilder, times defined from the central chart will be overwritten. To avoid this you have to perform a Get from Target before download, or you have to open the central time chart again and click ok to update the local time object once again.

Resolution

When you change a time in a central time schedule the change gets written down to the TAC Xenta Server time object the same way as a manual update.

After the correct time has been set in the TAC Xenta Server time object,  from the central time chart,  the controller will operate using these times until it gets new information. It does not matter if the connection to the TAC Vista Server is lost.

To perform get from target:

  1. In TAC XBuilder go to Project > Get from target
  2. Select "Get online changes"
  3. Click OK
Labels (2)
Labels:
  • Satchwell MicroNet
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 7692
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore