Vista Server trend logs, logging BACnet, M-bus or modbus values, are not updating
  • Vista Server trend logs, logging BACnet, M-bus or modbus values, are not updating
  • HenrikTarpgaard
    HenrikTarpgaard
‎2018-09-06 09:52 AM
  • Vista Server trends, logging BACnet, M-bus or modbus values, are not updating.
  • The same value being logged over and over.
TAC Vista
Xenta 700
TAC Xenta 913
This is due to a bug in the Xenta Server firmware, and happens if you have a menta application that uses other modbus values than the ones being logged.
If you open a graphic or the value columns the log works.
This issue will be fixed in 5.1.9.
5.1.8 hotfixes for Xenta 913 and Xenta 700 are available on request from PSS.
  • 14986