Vista - Menta error code Mainloop overrun. The application program can not execute within the specified cycle time

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Vista - Menta error code Mainloop overrun. The application program can not execute within the specified cycle time
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • sesa150561
    sesa150561

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1618 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Vista - Menta error code Mainloop overrun. The application program can not execute within the specified cycle time

Picard Product_Support
‎2018-09-06 10:51 AM

Issue

Occasionally get a alarm in Vista that is connected to the bit 16 of the error block in Menta (Mainloop overrun. The application program can not execute within the specified cycle time)

Environment

  • Vista
  • Menta
  • Xenta

Cause

In Menta under Program Specification there is a parameter called cycle time. This parameter tells how often the program should be run in the Xenta.
If the program take more time to execute then the specified value Vista will show a error connected to a error block in Menta, "Mainloop overrun. The application program can not execute within the specified cycle time" Vista will not show this specific text, Vista will show the text that you choose to show in the Alarm block connected to the Error block.

I.e. In Menta you have a error block that leads to a XPR block (expression block) that have the expression A&16, when this expression is meet it goes to the alarm block that will generate an alarm text of your choice. (16 is the bit that tells a Mainloop overrun. The application program can not execute within the specified cycle time have occurred.)

The Error block has several condition and work like this

The output of this block is an integer value where each bit represents an internal signal or error from the system program. Each output bit is set as long as the error condition remains, remains. In the case of a restart after a power failure, the output bit is set during the first program cycle after the restart. The output value is zero when no error conditions are set.

Conditions:

 

Bit no.

Output value

Description

0

1

Restart after power failure

1

2

Integer underflow/overflow

2

4

CNT block overflow

3

8

RT block overflow

4

16

Mainloop overrun. The application program can not execute within the specified cycle time

5

32

At least one of the switches on one of the I/O modules associated with the application, is in the position for manual override (ON, OFF, MAN) of the output

6

64

Indicates that an OP is connected, and the user is logged in at medium (yellow) or high level (red).

7

128

 

8

256

Dial-up modem line to TAC Xenta unit disabled

9

512

Update of a Network variable value was not received within the set Period

10

1024

There are tripped priority 1 alarms in the alarm list

11

2048

One or several I/O modules offline

12

4096

I/O in forced mode

13

8192

There are tripped and unacknowledged alarms in the alarm list

14

16384

There are tripped and not reset alarms in the alarm list

Resolution

To remedy this error change the cycle time to a higher value or make the Menta code lighter

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 11896
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of