There are no variables for forced value to trigger an object in a graphic.
In the graphic editor do as follow.
  1. Add a text object
  2. Add a binding to the text object and name it
  3. Change attribute to content
  4. Add a convert status
  5. Under behavior add text you want to show when the value its forced
  6. Edit binding for the graphic, bind the created textobject to the value of the point
The text object should now show the text forced when the value is forced.