Variable Connector

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Variable Connector
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • sesa139513
    sesa139513
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2299 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Variable Connector

Picard Product_Support
‎2018-09-06 03:48 PM

Issue

Problems with the speed a script was appearing to run. How to adjust the Variable Connector.

Environment

StruxureWare Building Operation site with BACnet or LON 

Cause

Definition of a variable connector

Problems with the speed a script was appearing to run

Resolution

Definition Variable connectors
The SmartStruxure system has a base philosophy where different objects and properties are connected using bindings. Bindings do not usually cause any significant load to the system, but in some cases the bindings need to be driven by an external object called a variable connector. The user does not create variable connectors.

The system creates variable connectors either when there is no obvious direction of the binding (analog value to analog value, for example) or when passing data between protocols (LonWorks to BACnet or LonWorks to Modbus).

Due to load caused by the variable connectors, limit the number of variable connectors according to the variable connectors table above. It is possible to increase this number, but close monitoring of CPU load and memory consumption is needed.

Release 1.4 Anticipated removal of Variable Connectors and replaced with a Binding Table. Variable Connectors cannot be removed. The maximum number of variable connectors is (Used when the binding has no obvious direction or when passing data between protocols)
Enterprise Server: No practical limit known
Automation Server:500

There are 'variable connector' objects in the system folder underneath the server that have a polling time associated with them and these are applied to both incoming and outgoing script variables. They default to 10 seconds polling time so regardless of the setting of a script cycle time it is subject to these polling times.

Note: The default value of 10 seconds polling time for values regardless of BACnet, LON or otherwise. 
Variable Connectors are automatically created when the bound values themselves are of a kind that lack the logic needed for polling. Editing the binding (by clicking the pencil icon next to the binding list path) indicates that there is a variable connector associated with the binding.  

Below is a screen capture for Variable Connector Settings.

Transfer Value Click the Force value button and enter the value that you want to force onto the binding.
Type Select how the binding is updated. Periodic polling updates the destination value at regular intervals. Change of value updates the destination value only when the source value changes, and only when the change is significant enough.
Interval Select the number of seconds between updates.
Propagation delta for value changes Enter how much the source value must change to trigger an update of the destination value.
Retransmit interval(s) Enter the number of seconds between forced updates.

In most cases, you bind a source value to a destination property that is an input variable in a program. The binding is direct, and the input variable actively reads the source value during every execution cycle of the program.However, not all bindings have a destination property that is an input variable in a program. When you create a binding, with a destination property that cannot read or poll the source value, StruxureWare creates a variable connector.
Most bindings do not need variable connectors, but when they do, StruxureWare creates them automatically.

There are basically three things you can do with a variable connector:
Configure polling method
Configure polling rate
Force the bound value

In a direct binding, you do not need to concern yourself with the polling of a bound value. There will be a program execution cycle involved that manages polling. With a variable connector you can configure the default polling settings in the properties of the variable connector. For more information, see Configuring a Variable Connector .

Also, in a direct binding, you may be able to force the bound value in the destination property. With a variable connector, you force the bound value in the properties of the variable connector.

Variable connectors and their properties are accessible from the Control Panel. There is a Variable Connectors list in the System folder of each server. Variable connectors are also accessible from the Binding point list.


LonWorks network variables and configuration properties can be bound to each other in LonWorks bindings. They can also be bound to most points in StruxureWare, such as programs, graphics, alarms, and trend logs, but then StruxureWare bindings is used, not LonWorks bindings.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • 7981
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore