Issue
The values read from an IAC600-S imported point are multiplied by 256.
Environment
StruxureWare
SNP
IAC
IAC600
IAC600-S
Values
Cause
The cause is believed to be the data bits for the value are read in the wrong order.
Resolution
This issue has been raise on the StruxureWare quality report system. (21033)
It is possible to correct this reading on a point by point basis with a simple script program.
1 numeric input A
2 numeric output B
3
4 B = A/256
Or with the use of a function block.

Linking the object to the input and the output then linked to the graphical display / log ETC.