Values from an Aaon device not showing up in Xenta Server Web Interface but work in the Vista Server
  • Values from an Aaon device not showing up in Xenta Server Web Interface but work in the Vista Server
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-06 10:14 AM
Values from an Aaon device not showing up in Xenta Server Web Interface but work fine in the Vista Server
Vista
XBuilder
Xenta Server
Vista will correct for xif files that do not strictly follow the LonMark Standard.  The Xenta Server does not include this feature.
The Aaon Chiller is not actually a LON device, but a BACnet IP device which is communicating to Lon Via a Field Server. The manufacturer provided xif file will function in Vista but not in the Xenta Server.
The only work around for this is to create the lon network in LonMaker and import that network into Xbuilder
  • 13797