Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Value Transfer Settings with Infinet Controllers

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Value Transfer Settings with Infinet Controllers
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • JohnBoehmer
    JohnBoehmer

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1688 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Value Transfer Settings with Infinet Controllers

JohnBoehmer Schneider Alumni (Retired)
‎2020-03-24 01:05 PM

Issue

Can Value Transfer Settings be used to control the frequency at which a value is transferred over the Infinet bus?

Product Line

EcoStruxure Building Operation, Andover Continuum

Environment

Continuum i2 Controller

Cause

There is a need to control the frequency at which a value is transferred from one Infinet controller to another.

Resolution

Whether or not the Value Transfer Settings determine the value transfer rate depends on the type of reference used.

When the Continuum to EBO transition process was developed, features and functionality were added to the Automation Server so that it would accommodate an existing controller protocol. Neither the Infinet controllers nor the Infinet protocol was substantially redesigned in order to work with Automation Servers.

Infinet controllers have never had a Value Transfer Setting capability and it was not added when the Continuum Transition process was developed.
The primary method of value transfer in Infinet controllers is the Import/Export tables. In order to enter a point into the Import Export table of a controller, the point has to be bound to an Infinet Script program or to an Infinity Alarm notification. You can find more information on the I/E functionality in the following Knowledge base article. Details on Continuum Import/Export (IE) System

The Import/Export system is a highly efficient means of value transfer that is base value change. If you chose to bypass the Import/Export capability, the only method available to you to control the frequency at which values are transferred over the Infinet bus is to read these values via a program that incorporates some form of throttling to slow down the polling rate.

Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • johnboehmer20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of