Using a temporary access control database during construction.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using a temporary access control database during construction.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Derrick_Ratliff
    Derrick_Ratliff
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1005 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using a temporary access control database during construction.

Picard Product_Support
‎2018-09-06 01:25 PM

Issue

During Construction it may be required to use a temporary database to allow access control to function before the IP infrastructure is in place.

Environment

I/NET Seven

Cause

A temporary database has been used during construction. The end user has an existing database that the new links and doors must be added to.

In some cases the temporary database may be required to be used while the building is occupied so a smooth transition between the two databases is required.

Resolution

Construction Phase

  1. Determine in advance the link information to be used for each new Xenta 527, and the full address for each door
  2. Determine who will access which doors within the new construction and add these individuals to new or existing groups accordingly
  3. Commission doors and add badges using the temporary database by using the available TAP on the SLI. If you use a crossover cable to connect to the Xenta 527, be sure to clear routing tables at the end of construction
  4. Ensure that each Xenta 527 has an available patch cable and Ethernet port installed
  5. Inform the IT department or installer that I/NET must have port 50069 open
  6. DO NOT leave the Xenta 527 plugged into the Ethernet port during construction
  7. If the building becomes occupied, add badges to the door using a temporary database connected via TAP
  8. If you are using multiple SLI's during the construction phase, it is important to ensure you are using only 1 access control Database.  Any other machine must have access control disabled to ensure cards are not removed from the system. If you have to add additional badges to any of the SLIs or change the temporary Database, you may need to do a station restore for the changes to take effect.

Adding the New Links and Doors to the existing system

  1. Verify that the Ethernet port by each Xenta 527 is functional by using a laptop to "ping" the Primary Host workstation. The lights on the Xenta 527 may show active Ethernet communication before the new construction IP is connected to the Local network.
  2. Connect to each controller using your temporary database. Perform a station save.  If you have any issues, this will function as your restore point.
  3. Connect to the Xenta 527 and ensure that the reference Hosts and link information is correct.
  4. Connect the Xenta 527 to the Ethernet port and cycle power.
  5. At the Host PC, Select Edit>Host Computer>Network Configuration
  6. Save the new Xenta 527's, SLI's, SCUs and Doors
  7. Select Access>Tenant
  8. Add the Doors to the appropriate Tenant
  9. Select Access>Groups
  10. Give the appropriate Groups access to the correct doors
  11. Verify you have given access to all appropriate people.  You may wish to compare the System View of each door on your temporary to the System View of each door on the site database
  12. Connect to the controller
  13. Select Edit>Controller>Station Save
  14. To clear the old database you will need to take the controller to Boot.
  15. select Edit> Host computer> software Restore
  16. Load the Bin file to the appropriate controller, but hit cancel after 10K have downloaded
  17. Load the Bin file again, this time allow it to finish.
  18. Connect to the controller
  19. Select Edit>Controller>Station Restore
  20. Choose the SLI option
  21. Select Edit>Controller>Station Restore
  22. Choose the DPU option
  23. Select all DPUs and restore
  24. Once this process is completed test several badges.
  25. Repeat steps 12-21 for each SLI under this Xenta 527
  26. Repeat this process for each Xenta 527
Labels (1)
Labels:
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • 5930
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore