Using a sound or visual notification of alarms in Vista Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using a sound or visual notification of alarms in Vista Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1265 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using a sound or visual notification of alarms in Vista Server

Picard Product_Support
‎2018-09-06 01:05 PM

Issue

How can a sound or light be triggered when an alarm or alarm type is active.

Environment

Vista 5.x.x.

Cause

Vista Server uses two sum alarm objects that control a database points for each alarm priority when they meet the criteria of the sum alarm type.

$Acoustic

Any alarm in that priority that requires an acknowledgement.

If acknowledgement reset is enabled then an alarm will trigger the Acoustic Sum Alarm a second time when it has returned to normal and requires a second acknowledgement.

$Optic

Active when any alarm in that priority is active or awaiting acknowledgement from a return to normal condition. Acknowledging the alarm does not stop the Optic Sum Alarm.

Resolution

To configure a sum alarm for control of physical objects such as a buzzer or light first setup the alarms to use a specific alarm priority.

Select either the $Acoustic or $Optic sum alarm in the TAC Vista folder or the Vista Server object and select the properties of the sum alarm object.

Select the browse button next to the priority of the alarms that match your criteria and browse to the database point that will trigger control logic or a physical output that results in an audible buzzer or a visible light. To send a value to multiple controllers use an internal database point then use Object Transfer to send it to multiple controllers for control of physical equipment.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 6587
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of